The realistic 12-month picture
A typical 200-500 kWp UK office solar project takes 9-12 months from initial enquiry to commissioning. The steps and dependencies are well-established; understanding them helps project sponsors plan capex cycles and tenant communications.
Month-by-month breakdown
Month 1: Feasibility and proposal
- Half-hourly meter data request to DNO/supplier (ask the supplier or DNO how long it will take)
- Site visit and structural / roof assessment
- PVSyst yield modelling
- Planning route assessment
- Fixed-price proposal with all four funding routes
Customer decisions: funding route selection, scope decisions (battery yes/no, EV charging yes/no).
Month 2: Contract and design
- Detailed design phase
- Structural engineering sign-off
- Electrical design (string layout, inverter selection, cabling routes, switchroom modifications)
- Project programme finalisation
Customer decisions: install timing preferences (out-of-hours, weekend, summer-only), tenant communication strategy.
Month 3-4: Planning and DNO application
- Planning route execution: Permitted Development (no application), Prior Approval (56 days), full planning (8-13 weeks), Listed Building Consent (8-13 weeks)
- G99 grid connection application (DNO response time varies by network and by application; ask the DNO, or any installer you are comparing, for its current G99 timescale)
- Pre-application consultations with conservation officers (heritage settings)
Customer involvement: Minimal — the installer typically manages the applications.
Month 5-6: Approvals and procurement
- Planning / Prior Approval determination
- DNO G99 acceptance
- Equipment procurement (panels, inverters, mounting, switchgear) — typical 8-12 week lead time on Tier-1 manufacturer products
- Site mobilisation planning
Customer involvement: Tenant communication if relevant.
Month 7-9: Installation
- Site mobilisation (typically 1 week)
- Mounting system installation (2-3 weeks for 300 kWp typical)
- Panel installation (1-2 weeks)
- Electrical installation (2-3 weeks)
- Commissioning testing (1 week)
Customer involvement: Site access coordination, parking management.
Month 10: Commissioning and grid connection
- Final inverter commissioning to IEC 62446
- DNO witnessing visit and connection approval
- Generation start
- Performance monitoring setup
- Customer training session
Customer involvement: Half-day commissioning attendance recommended.
Month 11-12: Handover and documentation
- 30-day post-commissioning performance review
- Documentation handover (electrical certs, structural certs, warranty certs, monitoring access)
- Scope 2 Disclosure Pack delivered
- SEG tariff registration
- O&M contract activation
Customer involvement: Document storage and tenant onward communication.
What drives schedule
Three factors materially affect timeline:
1. Planning route. Permitted Development can shave 3 months; full planning permission in heritage settings can add 3-6 months versus baseline.
2. DNO grid connection. G99 acceptance time varies by network and by application, and it can be much longer where the network is constrained; ask the DNO for its current G99 timescale for your postcode. Always file G99 early — it runs in parallel with planning, so doesn’t directly add to programme.
3. Customer decision speed. From proposal to contract signing, customers typically take 4-12 weeks. Faster customers (sub-4 weeks) compress overall timeline; slower customers (12+ weeks) extend it linearly.
When the timeline compresses
A well-run UK office solar project can get from feasibility to commissioning in under six months. The conditions:
- Permitted Development (no application needed)
- DNO connection in an area with spare network capacity (G99 acceptance without a network study)
- Standard equipment availability (no Tier-1 product shortages)
- Customer ready capex available (no financing approval cycle)
- Strong project management on the customer side
Five months is achievable but exceptional. Most projects benefit from a 9-12 month planning horizon.
What happens when timelines slip
The biggest schedule risk is DNO grid connection in constrained networks. Where the local DNO indicates G99 acceptance will take much longer than your programme allows, options include:
- Stage 1 install at reduced output limit: Install full system but commission at reduced export, increase output when DNO grid availability allows.
- Export-limited or zero-export design: Install the full array with an export limitation scheme, which can let the DNO approve the connection without waiting for network reinforcement. The G99 application is still needed: the G98 limit of 16A per phase applies to the size of the system, not to how much it exports.
- Wait for DNO upgrade: Some areas have committed DNO investment programmes that will resolve constraints; ask the DNO whether one covers your postcode and when it is due.
Your installer should engage with the DNO from early proposal stage to understand the constraint position and recommend the right strategy.
Send us your building details; we reply by email.
Critical path analysis: the dependencies that drive schedule
Project management of commercial solar requires understanding not just what needs to happen but what depends on what else. The true critical path — the sequence of dependent tasks that determines the earliest possible completion date — typically runs through DNO grid connection.
Critical path dependency chain for a 300 kWp office solar project:
- Feasibility and proposal — cannot start until site visit scheduled
- Contract award — depends on customer decision
- G99 application submission — can only be submitted after DNO connection design is complete, which requires system design, which requires contract award
- G99 DNO response — the timescale varies by network and by application; ask the DNO for its current G99 timescale
- Equipment procurement — can run in parallel with G99; 8-12 week typical lead time on Tier-1 equipment
- Planning approval — can run in parallel with G99; Prior Approval is 56 days; full planning is 8-13 weeks
- Installation — cannot start until G99 approved, planning approved, and equipment delivered
- DNO commissioning witnessing — where the DNO requires a witnessing visit, it must happen before grid connection can be activated
- Generation start
The dependencies reveal why G99 is almost always the critical path: it cannot start until design is complete (requiring contract award), takes a time set by the DNO that varies by network and by application, and installation cannot commence until G99 is approved. Everything else — equipment procurement, planning, detailed design — can run in parallel with G99.
How to compress the timeline
For project sponsors wanting to achieve faster commissioning, five actions materially reduce programme length:
1. Pre-application DNO enquiry. Before contract award, submit an informal enquiry to the DNO identifying the proposed connection point and indicative system size. Ask the DNO how long it takes to respond to pre-application enquiries; the response can flag any constraints, required studies, or connection cost contributions that would affect project economics. This reduces surprises at formal G99 application stage and allows G99 submission immediately after contract award rather than after a further wait.
2. Pre-planning enquiry. Many local planning authorities offer Pre-Application Planning Advice (PAPA) services for commercial applications. For projects where planning route is uncertain (mixed heritage settings, Conservation Area adjacency, sites near residential properties), a PAPA response (typically 4-8 weeks, 500-1,500 fee) confirms the correct application route and identifies any key design requirements before full design investment. It eliminates planning refusal or amendment cycles later.
3. Long-lead equipment pre-order. Tier-1 solar panels (LONGi, JinkoSolar, Trina) have 8-12 week lead times from order to UK delivery. Where the project scope is well-defined at contract award, placing panel and inverter orders at contract award rather than waiting for G99 approval can shorten the overall programme. Risk: if G99 approval is refused or major scope changes are required, pre-ordered equipment may need to be resold or respecified. This risk is typically small on well-designed projects in non-constrained network areas.
4. Customer-side decision speed. The table below shows how customer decision timing affects overall programme:
| Customer decision speed | Additional weeks added |
|---|---|
| Contract signed within 2 weeks of proposal | 0 |
| Contract signed in 3-5 weeks | +1-3 |
| Contract signed in 6-9 weeks | +4-7 |
| Contract signed in 10-12 weeks | +8-10 |
| Contract signed in 13+ weeks | +11+ |
This is rarely discussed in project management conversations but is frequently the largest controllable schedule variable. Customers whose capex budget is already signed off and streamlined internal approval processes consistently commission 2-3 months earlier than customers requiring full board cycle approval.
5. Commissioning scheduling. Where the DNO requires a commissioning witnessing visit, it needs booking in advance; ask the DNO how much notice it needs. Pre-booking the witnessing visit during the installation phase (rather than after installation is complete) removes a gap at the end of the programme. Ask the DNO whether it will accept a conditional pre-booking.
COVID and supply chain impacts on 2026 timelines
The 2021-2023 supply chain disruptions significantly extended commercial solar timelines. Understanding what has normalised and what has not helps set realistic 2026 expectations.
Normalised by 2026:
- Shipping timelines from China (returned to 5-7 week ocean freight vs 12-16 weeks at peak congestion)
- Inverter supply (Huawei, Sungrow, Solis all have UK stock positions)
- Panel supply for Tier-1 manufacturers (significant capacity expansion means UK distributors hold substantial stock)
- UK installation labour (installation firms have rebuilt capacity post-COVID disruption)
Still extended versus pre-2020 baseline:
- Battery storage for large commercial systems (200 kWh+): Tesla Powerwall, BYD Battery-Box, Huawei LUNA all have 12-20 week lead times for large commercial orders
- Specialist switchgear (low-voltage switchboards, export limiting relay equipment): 10-16 week lead times for some configurations
- DNO response times in constrained areas (a network capacity issue, not a supply chain issue; ask the DNO for its current G99 timescale)
For projects including battery storage, add 8-12 weeks to the procurement timeline versus storage-free projects. This is the most common cause of programme extension on 2026 UK commercial solar projects.
When the programme slips: managing stakeholders
Three communication steps that prevent programme delays from becoming stakeholder crises:
1. Issue a programme at contract award. The programme should show the G99 application date explicitly, the expected G99 response date, and the consequent earliest installation start. If stakeholders understand from the outset that G99 drives schedule, they are better prepared when the DNO takes longer than expected.
2. G99 progress update at the midpoint. Ask the DNO when it expects to respond to the G99 application and, at the midpoint of that period, contact the DNO’s assigned case officer for a status update. The DNO should be able to say whether its review is straightforward (pointing to fast resolution) or complex (flagging a possible network study requirement).
3. Communicate installation start date 4 weeks in advance. Building managers need 4 weeks to arrange tenant communications, parking management, lift access coordination, and security briefings for installation crews. Late installation start notification is one of the most common sources of client frustration on well-managed projects.
What makes a programme fast or slow
This site is an independent guide, not an installer, so it has no completed projects of its own to time. The conditions below are the ones that usually separate a short programme from a long one; use them to judge where your building sits.
What shortens a programme: Permitted Development (no planning application), a network area with spare capacity so the G99 offer needs no network study, equipment from UK distributor stock, a single owner-occupier with capex already approved, and an experienced installation team. A G99 application is still part of the fast case: G98 covers only systems up to 16A per phase (about 3.68 kW single-phase, about 11 kW three-phase), so an 80 kWp office array, like almost every office roof, needs a G99 application approved by the DNO before connection.
What lengthens a programme: a listed building in a Conservation Area that needs full planning permission and Listed Building Consent (longer again if either is refused and resubmitted), a G99 application on a constrained network where the DNO asks for a reinforcement contribution, and financing that needs more than one board cycle.
For a 100-500 kWp office outside heritage settings, the 9-12 month horizon at the top of this guide is a planning assumption, not a measured average. Ask your DNO for its current G99 timescale for your postcode before you fix a programme date.
Key takeaways
- G99 DNO application is almost always the critical path for commercial solar; it cannot start until system design is complete and its duration varies by network and by application
- Pre-application DNO enquiry (before contract award) is the single most powerful schedule compression tool
- Customer decision speed is a significant controllable variable: sub-2-week contract turnaround versus 10+ weeks can shift commissioning by 2-3 months
- Battery storage adds 8-12 weeks to procurement timeline in 2026 — account for this in programmes including storage
- DNO response times differ between networks and between applications; ask the DNO for its current G99 timescale for your postcode rather than relying on a published average