Office roof data

Office roof solar check: yield, cost and planning data for UK offices

Four public datasets in one place, and a check that turns your roof area into a system size, a yearly generation figure, a cost reference and the planning route. No sales pitch; we reply by email if you send it.

Office roof plans being reviewed for a solar PV layout

Run the check for your building

The check uses the same four datasets as the tables below. It needs only a roof area and your nearest city; add the floor area and your unit rate for the share of use and the value. The estimate shows on the page as you type. Sending it is optional.

How the estimate is worked out

  1. Clear roof area = roof area × the share clear of plant (70%, 50% or 30% from your answer). This is an assumption you can change by choosing a different option.
  2. System size (kWp) = clear area ÷ 5 m² per kWp (5.5 m² on mixed roofs). Modern modules of around 430 W are a little under 2 m² each; the allowance covers gaps, walkways and row spacing.
  3. Yearly generation = kWp × the PVGIS yield for your nearest office market and roof type (flat roofs as a 10° east-west layout, pitched roofs at 30° south, mixed roofs at 10° south).
  4. Share of use = generation ÷ (floor area × 95 kWh per m², the CIBSE TM46 general-office electricity benchmark).
  5. Cost reference = kWp × the DESNZ 2025/26 non-domestic average (mean) for that size band, up to 50 kW. Above 50 kW the check states the 10-50 kW average as a reference only.
  6. Planning route = the Class J tests for England (listed status, size over or under 50 kW, Article 4 note for conservation areas), or the devolved class that applies instead: Part 43 Class A in Wales, Class 6J in Scotland or Part 37 Class A in Northern Ireland.

Dataset 1: solar yield for 13 UK office markets

Pulled from the European Commission's PVGIS v5.2 on 18 October 2026 for 1 kWp of crystalline silicon panels on a free-standing rack with 14% system losses, using the PVGIS-SARAH2 radiation database. The last column scales the east-west figure to 100 m² of clear flat roof at 5 m² per kWp, which is 20 kWp.

Annual yield by office market, kWh per kWp
Office marketNationNetwork operator10° east-west10° south30° southkWh a year per 100 m² clear flat roof
CardiffWalesNational Grid Electricity Distribution853933102117,060
ReadingEnglandSSEN (Southern Electric)849929101716,980
London (City)EnglandUK Power Networks848928101816,960
BristolEnglandNational Grid Electricity Distribution848927101416,960
CambridgeEnglandUK Power Networks846930102716,920
BirminghamEnglandNational Grid Electricity Distribution80588096416,100
NottinghamEnglandNational Grid Electricity Distribution80488196916,080
LeedsEnglandNorthern Powergrid77585093815,500
NewcastleEnglandNorthern Powergrid76284193615,240
BelfastNorthern IrelandNIE Networks75682891015,120
ManchesterEnglandElectricity North West74280788014,840
EdinburghScotlandSP Energy Networks74081690514,800
GlasgowScotlandSP Energy Networks70777184314,140

Source: PVGIS v5.2 PVcalc, European Commission Joint Research Centre (re.jrc.ec.europa.eu). Sorted by the east-west column. Coordinates are city-centre points; shading and module choice change real output.

Three things stand out for office owners. First, the spread is real but not decisive: Cardiff tops the east-west column at 853 kWh per kWp and Glasgow is lowest at 707, a gap of about 17%. A Glasgow office with a clear roof still out-generates a London office whose roof is crowded with plant. Second, Leeds (775) beats Manchester (742) despite being further north, which is why a city-specific figure matters more than a north-south rule of thumb. Third, on a flat roof in central London, south-facing rows at 10° yield about 9% more per kWp than an east-west layout (928 against 848 kWh), but east-west rows need far less spacing and pack more panels into the same area, which is why so many office roofs use them.

Dataset 2: how far the roof goes, by number of storeys

This is the question estates teams ask first: what share of the building's electricity can the roof supply? Holding everything else equal (a roof half clear of plant, 5 m² per kWp, the east-west yield and the TM46 benchmark of 95 kWh per m² of floor), the answer is driven by the number of storeys, because each extra floor adds demand but no roof.

Share of benchmark office electricity covered by a half-clear roof
StoreysCentral LondonManchesterGlasgow
189%78%74%
245%39%37%
422%20%19%
811%10%9%

Calculated from PVGIS v5.2 yields and the CIBSE TM46 general-office electricity benchmark (95 kWh/m²). A building with lower use than the benchmark, or a clearer roof, covers more.

The practical reading: single-storey business-park offices can cover most of their daytime use from the roof, while a mid-rise city office should size the array to displace daytime demand and look to a car-park canopy, a PPA or efficiency measures for the rest. Neither case needs a battery to use the output, because an office's use runs through the working day.

Dataset 3: what the official statistics say about cost

DESNZ publishes the UK's only official solar cost series, built from Microgeneration Certification Scheme records. The 2025/26 release covers April 2025 to March 2026 and was published on 28 May 2026. It reports 88,788 non-domestic installations, 4,368 of them in the 10-50 kW band.

Installed cost per kW, 2025/26: non-domestic mean and all-installation median
Size bandNon-domestic (mean)All installations (median)
0-4 kW£1,892£1,780
4-10 kW£1,533£1,697
10-50 kW£1,259£1,262

Source: DESNZ, Solar PV cost data 2025/26 (declared net capacity basis). Includes equipment, installation, grid connection and VAT where applicable; excludes battery storage. DESNZ gives the non-domestic breakdown as a mean and publishes medians only for all installations combined, so the two columns are different statistics. No official series exists above 50 kW.

Two cautions. The figures include VAT where it applied, so compare like with like when you read a quotation. And because most office systems are larger than 50 kW, the honest use of these numbers is as an upper reference for a first budget line. A proposal priced from your meter data and a roof survey replaces it.

Dataset 4: the planning route, situation by situation

For England, the rules are in Class J of Part 14, Schedule 2 of the Town and Country Planning (General Permitted Development) (England) Order 2015, checked against the latest revised text on legislation.gov.uk on 18 October 2026.

Office rooftop solar: planning route in England
SituationRouteWhat it means in practice
Rooftop system up to 50 kW, building not listedPermitted development, Class JNo application, provided panels stay within 1 m of the highest part of a flat roof (0.2 m beyond a pitched slope) and at least 1 m from the roof edge
Rooftop system above 50 kWClass J(c) with prior approvalApply to the council, which considers design, external appearance and glare on neighbours and has 56 days to decide
Listed building, or within its curtilageNot permitted developmentListed building consent, and usually planning permission
Scheduled monument siteNot permitted developmentA planning application and scheduled monument consent
Conservation area, not listedClass J still applies to roofs: the roof-slope-fronting-a-highway exclusion on article 2(3) land (J.1(d)) was omitted on 21 December 2023 (S.I. 2023/1279, art. 6(2))Check whether an Article 4 direction removes the right in your area
Very large rooftop systemNo capacity capThe 1 MW limit in J.3 was omitted on 21 December 2023 (S.I. 2023/1279, art. 6(3))
Wales, Scotland or Northern IrelandDevolved rulesClass J is England only; check your nation's permitted development order with the council

Source: GPDO 2015 Sch. 2 Pt 14 Class J (J.1, J.2, J.4), latest revised version on legislation.gov.uk. This is a summary, not legal advice; the council's view decides.

The detail behind each route, including Article 4 directions and listed offices, is in the planning permission guide for commercial buildings.

Before the numbers: who confirms each roof check

Office roof checks and who signs them off
CheckWhy it matters on an officeWho confirms it
Remaining roof lifeLifting an array to re-roof costs money and downtimeRoofing contractor or building surveyor
Load and wind upliftBallast adds weight; lightweight and modular offices are the usual limit (see modular offices)Structural engineer
Plant and rooflightsChillers, AHUs and lift rooms cut the usable areaFacilities manager, with a roof plan
ShadingTaller neighbours to the south can take a large share of outputYield model with a shading survey
Fire strategy and accessCable routes, isolation and safe access affect design and insuranceFire engineer and the building's insurer
Grid connectionG98 covers small systems; most office arrays need a G99 applicationYour distribution network operator

For flat roofs specifically, the flat-roof office guide covers ballast and membrane questions, and the guide to how many panels an office needs goes deeper on sizing from meter data.

Use and cite this data

The tables on this page may be quoted with a link. Cite as: Office roof solar check, solarpanelsforofficebuildings.co.uk, last verified 18 October 2026; yields from PVGIS v5.2 (European Commission JRC), costs from DESNZ Solar PV cost data 2025/26, demand from CIBSE TM46, planning from the GPDO 2015 on legislation.gov.uk. We re-pull the yields and re-check the cost release and the legislation when they change. This site is an independent guide published by SEO Dons Ltd; it is not an installer.

Questions about office roofs and solar

Frequently Asked Questions

How do I know if my office roof is suitable for solar panels?

Check five things in this order: the roof covering has plenty of life left, a structural engineer confirms it can carry the extra load and wind uplift, there is enough clear area once plant, rooflights and a 1 m edge zone are excluded, nearby buildings do not shade it heavily, and the grid connection is workable. The office solar check on this page turns the clear area and your nearest city into a system size and yearly generation.

How much electricity does a solar panel system on an office roof generate?

PVGIS v5.2 gives between 707 kWh (Glasgow) and 853 kWh (Cardiff) per kWp a year for a flat-roof 10° east-west layout across the 13 UK office markets in the table, and 1018 kWh per kWp in central London for a pitched roof at 30° facing south. Multiply by the system size in kWp for a yearly figure.

What share of an office building's electricity can rooftop solar cover?

It depends mostly on the number of storeys. Using the CIBSE TM46 general-office benchmark of 95 kWh per m² and a roof half clear of plant, a single-storey office in central London could cover about 89% of its use, a four-storey office about 22% and an eight-storey office about 11%.

How much does office rooftop solar cost per kW?

The official benchmark is DESNZ Solar PV cost data. For 2025/26 the average (mean) installed cost for non-domestic systems of 10-50 kW was £1,259 per kW. DESNZ publishes no series above 50 kW, where prices per kW are usually lower, so use the 10-50 kW average as a reference rather than a quote.

Does office rooftop solar need planning permission?

In England, Class J of Part 14 of the GPDO 2015 makes rooftop solar on non-domestic buildings permitted development, except on listed buildings and scheduled monuments and subject to height and 1 m edge limits. Above 50 kW, Class J(c) needs prior approval from the council on design, external appearance and glare, decided within 56 days. Wales, Scotland and Northern Ireland have their own rules.